Marine Electrical Oral Questions & Practical Answers (Generators & Switchboard)
⚡ Generator & Switchboard
Oral Questions & Practical Answers (Marine Electrical)
Written by Seafarers, for Seafarers ⚓
Focused on real onboard practice, not book definitions.
1. What does the different position of the synchroscope needle mean?
What is the difference between 6 o’clock and 12 o’clock?
- 6 o’clock → Generator is out of synchronisation.
Voltage, frequency or phase sequence do not match.
❌ Paralleling is not allowed. - 12 o’clock → Perfect synchronisation.
Voltage, frequency and phase sequence match.
✅ Generator can be paralleled.
2. Why do we close the breaker at 11 o’clock and not exactly at 12 o’clock?
Because of mechanical closing delay.
- When the needle approaches 12 o’clock, slip is very small.
- The breaker takes a short time to close.
- If we press close at 11 o’clock, the breaker actually closes near 12 o’clock.
👉 This ensures smooth synchronisation without shock loading.
3. What is slip during synchronisation?
Slip is the
difference in frequency between:
- incoming generator
- bus bar
Slip becomes zero at 12 o’clock position.
4. Why is a Megger used instead of a multimeter for insulation testing?
- Megger uses high DC voltage (usually 500V or 1000V).
- Multimeter uses very low voltage (2–3V DC).
Low voltage cannot detect weak insulation.
Megger gives a real insulation resistance value.
5. What are the main safeties provided on the Main Switchboard (MSB)?
- Circuit breakers
- Fuses
- Overcurrent protection relays
- Reverse power protection
- Earth fault indication
MSB panels are dead-front type, meaning:
- You cannot access live parts during normal operation.
6. What is reverse power flow?
Reverse power occurs when:
- Generator terminal voltage drops below bus voltage
- Generator starts acting like a motor
- Power flows from bus bar to generator
This condition is dangerous for the prime mover, not the generator.
7. What is the harm caused by reverse power?
- Generator absorbs power instead of producing it
- Sudden step increase of load on the system
- Possible frequency drop
- Risk of prime mover damage (especially steam turbines)
8. How is protection against reverse power provided?
By Reverse Power Relay:
- Detects reverse power condition
- Trips the generator breaker
- Cuts fuel supply to the prime mover
👉 Purpose: anti-motoring protection
9. How do you test reverse power trip onboard?
When two generators are running in parallel:
- Slowly reduce load on one generator using governor
- When load becomes very small, breaker trips
- Fuel supply cuts off
Alternatively:
- Test relay using relay test button / simulation mode
10. What is ACB and where is it used?
ACB – Air Circuit Breaker
- Used for high current applications
- Commonly used as generator breaker
- Typically for 400V systems
11. What happens if you press the ACB close button on an idle generator?
Normally nothing happens.
Because:
- Synchronisation conditions are not met
- Under-voltage protection prevents closing
This avoids accidental paralleling.
12. What is under-voltage protection?
It prevents:
- Closing breaker when generator voltage is low
- Damage to equipment
- Accidental closing during parallel operation
Also protects loads during voltage failure.
13. What is preferential trip and why is it provided?
Preferential trip:
- Automatically disconnects non-essential loads
- Keeps essential services running
Examples:
- Trips: galley, air conditioning
- Keeps: steering gear, navigation, pumps
👉 It is a critical safety feature.
14. What is the purpose of earth fault indication on switchboard?
- Detects phase-to-earth fault
- Gives alarm without immediate blackout
- Allows controlled fault finding
15. What should you do if you get an earth fault alarm?
- Identify high-risk areas (deck lights, pantry, wet spaces)
- Isolate circuits one by one
- When alarm clears → faulty circuit identified
- Repair before re-energising