Oral Questions & Practical Answers (Marine Electrical)

Written by Seafarers, for Seafarers
Focused on real onboard practice, not book definitions.


1. What does the different position of the synchroscope needle mean?

What is the difference between 6 o’clock and 12 o’clock?

  • 6 o’clock → Generator is out of synchronisation.
    Voltage, frequency or phase sequence do not match.
    ❌ Paralleling is not allowed.
  • 12 o’clockPerfect synchronisation.
    Voltage, frequency and phase sequence match.
    ✅ Generator can be paralleled.


2. Why do we close the breaker at 11 o’clock and not exactly at 12 o’clock?

Because of mechanical closing delay.

  • When the needle approaches 12 o’clock, slip is very small.
  • The breaker takes a short time to close.
  • If we press close at 11 o’clock, the breaker actually closes near 12 o’clock.

👉 This ensures smooth synchronisation without shock loading.


3. What is slip during synchronisation?

Slip is the

difference in frequency between:

  • incoming generator
  • bus bar

Slip becomes zero at 12 o’clock position.


4. Why is a Megger used instead of a multimeter for insulation testing?

  • Megger uses high DC voltage (usually 500V or 1000V).
  • Multimeter uses very low voltage (2–3V DC).

Low voltage cannot detect weak insulation.
Megger gives a real insulation resistance value.


5. What are the main safeties provided on the Main Switchboard (MSB)?

  • Circuit breakers
  • Fuses
  • Overcurrent protection relays
  • Reverse power protection
  • Earth fault indication

MSB panels are dead-front type, meaning:

  • You cannot access live parts during normal operation.


6. What is reverse power flow?

Reverse power occurs when:

  • Generator terminal voltage drops below bus voltage
  • Generator starts acting like a motor
  • Power flows from bus bar to generator

This condition is dangerous for the prime mover, not the generator.


7. What is the harm caused by reverse power?

  • Generator absorbs power instead of producing it
  • Sudden step increase of load on the system
  • Possible frequency drop
  • Risk of prime mover damage (especially steam turbines)


8. How is protection against reverse power provided?

By Reverse Power Relay:

  • Detects reverse power condition
  • Trips the generator breaker
  • Cuts fuel supply to the prime mover

👉 Purpose: anti-motoring protection


9. How do you test reverse power trip onboard?

When two generators are running in parallel:

  1. Slowly reduce load on one generator using governor
  2. When load becomes very small, breaker trips
  3. Fuel supply cuts off

Alternatively:

  • Test relay using relay test button / simulation mode


10. What is ACB and where is it used?

ACB – Air Circuit Breaker

  • Used for high current applications
  • Commonly used as generator breaker
  • Typically for 400V systems


11. What happens if you press the ACB close button on an idle generator?

Normally nothing happens.

Because:

  • Synchronisation conditions are not met
  • Under-voltage protection prevents closing

This avoids accidental paralleling.


12. What is under-voltage protection?

It prevents:

  • Closing breaker when generator voltage is low
  • Damage to equipment
  • Accidental closing during parallel operation

Also protects loads during voltage failure.


13. What is preferential trip and why is it provided?

Preferential trip:

  • Automatically disconnects non-essential loads
  • Keeps essential services running

Examples:

  • Trips: galley, air conditioning
  • Keeps: steering gear, navigation, pumps

👉 It is a critical safety feature.


14. What is the purpose of earth fault indication on switchboard?

  • Detects phase-to-earth fault
  • Gives alarm without immediate blackout
  • Allows controlled fault finding


15. What should you do if you get an earth fault alarm?

  1. Identify high-risk areas (deck lights, pantry, wet spaces)
  2. Isolate circuits one by one
  3. When alarm clears → faulty circuit identified
  4. Repair before re-energising